Northern Rancher said:
Most fencers aren't grounded right around the country.
I believe the figure is around 85% that aren't sufficient.
On all fences I install, I now add an earth wire return.
I don't get dry enough conditions for it, but we do get snow and ice which has the same effect. I think pouring water on your ground rods is a waste of time. When the animal hits a live wire only, it goes through the animal, through the ground to the grounding "antenna". That water you pour on the rod only soaks a few inches away from the rod. You still have all that space between there and the animal that didn't get soaked. If you do have dry, poor soils you can buy super grounding kits. It's a tube you bury and pound your ground rod into. Helps the conductivity in poor soils.
http://www.gallagherusa.com/electric-fencing/permanent.component.aspx?mktprodid=1378
One other tip. Rent a hammer drill, I bought one with a SDS Max chuck, and get a ground rod driver for it. Switch it to hammer only and vibrate the rod into the ground. I installed like 10 rods on a 25 joule MBX 2500 charger. The last two hit bedrock or something. I just put my weight on the hammer drill and spent more time, but eventually got them in.
If you have a metal culvert somewhere, run a ground wire to that, that's about the best ground you can get.
Download the Gallagher Manual. Grounding information starts on page 18, should be everything you need to know.
http://www.gallagherusa.com/common/...978-Powerfence-US-Ed1&internal=true&extn=.pdf
Highlights
10-3-6-1 Rule for Ground rods :
10 Feet between ground rods
3 Ground rods minimum required
6 Feet min. length of ground rod
1 Wire connecting all ground rods
Energizer Size Ground rods
required
Up to 15 J 3 Stakes minimum
Up to 25 J 5 Stakes minimum
Up to 35 J 7 Stakes minimum
Location of the ground system
The most effective place for the ground
system is in continuously damp, high
mineral soil.
• At least 33ft from an electrical or
telephone ground (the further away the
better)
• At least 33ft from metal pipes carrying
domestic or stock water
• At least 66ft from any dairy shed pipe
work
• Not connected to, or touching steel or
iron clad buildings
• Protected from machinery and stock
damage
• Away from fertilizer, animal urine and
manure (corrosion)
TESTING
Test the ground system
This needs to be done once a short section
of fence has been built. It should be tested
at least once a year or at the height of any
dry period to ensure the grounding capacity
is sufficient for the joule rating of the
energizer.
Short the fence out at least 330ft away
from the ground system by using several
steel stakes between the hot wires and the
ground. Reduce the fence voltage at this
point to 2000V (2kV) or less.
Using a Digital Volt Meter (DVM) (G5030 or
G5035) measure the voltage between the
wire connecting through the ground rods
to the energizer ground terminal and an
independent ground rod. This stake should
be a galvanized metal rod, minimum 8"
long, and placed 3ft away from the ground
rods or as far away as your DVM cable will
reach (see Figure 4.9).
Note: If you are using a SmartPower
energizer the ground monitor/alarm will
indicate when the ground system requires
attention (see Figure 4.6).
There should be no reading on the DVM,
however up to 200V (0.2kV) is acceptable.
If the voltage is higher than this, switch off
the energizer, drive in more ground rods at
the recommended spacings and connect
them to the existing ground system until
the voltage is down to the acceptable level.